Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Baxi instant 105e Diverter valve repair in the Air Sourced Heat Pumps area at Plumbers Forums

Messages
13
Hi all,
Quick question. I have a baxi 105e instant that has a Diverter valve issue. The bypass is allowing hot water around the bypass pipe and into the CH return pipe. I have looked at a rebuild kit and it seems that there are 2 listed. One is a cartridge type and the other more a kit. My question
Is, can the cartridge replace the older style sliding spool or are they not interchangeable ?
Thanks
Roseyp
 

Attachments

  • 78AE5131-0B28-4C12-9364-DD9E54422F3D.jpeg
    78AE5131-0B28-4C12-9364-DD9E54422F3D.jpeg
    578.2 KB · Views: 46
  • 8EF9AFAB-2C7F-440B-83A0-4AFFD94EC7CA.jpeg
    8EF9AFAB-2C7F-440B-83A0-4AFFD94EC7CA.jpeg
    1.3 MB · Views: 34
One on the right is for an external bypass but you have to check the hot water plate isn’t blocked as this will have the same symptoms
 
One on the right is for an external bypass but you have to check the hot water plate isn’t blocked as this will have the same symptoms
Hot water flow rate is good, no change really just taking longer to warm up. Boiler deffo has the external bypass as I can feel the pipe getting hot as soon as the dhw fires up. Goes from the rear of the Diverter to the rear of the ch return manifold. I will drop the plate heat exchanger out as I have new seals, but it either rebuild the Diverter with the kit, or get a new Diverter valve. Trouble will be the part numbers seem the same for the valve whether it’s an external or internal bypass, so I need to ensure that I get the correct one
Thanks for help though
Roseyp
 
A refurb valve is only £35 so maybe go that route. This is only a stop gap as I’m looking to get the boiler replaced before Xmas
Thanks again
Roseyp
 

Attachments

  • 91D65200-6ACC-46BA-9480-53CB0DCA01E2.jpeg
    91D65200-6ACC-46BA-9480-53CB0DCA01E2.jpeg
    234.8 KB · Views: 25
Do you have to send the old one back ?
 

Similar plumbing topics

Upto you the duo has a flow rate of 11 as the...
Replies
4
Views
2K
I've tidied up this thread and banned a user...
Replies
2
Views
739
  • Question
Closing the loop... I replaced the valve body...
Replies
6
Views
2K
  • Question
After some consideration 15mm plastic with...
Replies
12
Views
5K
Back
Top