B bewsh Plumbers Arms member Plumber Gas Engineer Messages 608 Nov 12, 2015 #1 Got a flue to change on the above boiler next week. The flue exits on the right hand side of the boiler. Does the boiler need to come off the wall to replace or can you do it in situ? Cheers!
Got a flue to change on the above boiler next week. The flue exits on the right hand side of the boiler. Does the boiler need to come off the wall to replace or can you do it in situ? Cheers!
E Elgordo Gas Engineer Messages 101 Nov 14, 2015 #2 There is a bayonet fitting on the flue pipe so once you free up the flue outside it should twist and pull out -in theory - download the installation manual , it's fairly well covered .
There is a bayonet fitting on the flue pipe so once you free up the flue outside it should twist and pull out -in theory - download the installation manual , it's fairly well covered .