How's it going guys? Just want to pick your brains. My mate went to a baxi solo 3 50pf because the fan had failed, he replaced the fan and it was working fine, now they say that since the fan has been changed the boiler keeps overheating. So I went over today to have a look thinking it was probably the pcb pump overrun. But after looking at it, when you turn the c/h on the mid pos moves fine, but you knock it off and you still get 210vac on the orange to the boilers s/l and the boiler stays on. I tested all the controls, room stat, programmer, cylinder stat and they all proved to be ok, so thought it must be a faulty mid pos giving power to the orange with no demand. But am I right in thinking that of it's still giving power to the boiler, then the pump should also continue running? Cheers guys