Evening all,
next door has a problem with their Baxi Solo 3 60 pf.
Unbeknown to me other engineers have looked at the boiler, and I am now told they said it was the programmer but would not come back to replace.
New build block of apartments with underground parking, each having a boiler room with a baxi solo and unvented water cylinder, 1 heating zone for the bedrooms/ bathrooms another pump station for the under floor heating. Approx 8/9 years old.
I popped in last week and could not get the boiler to fire, correct voltage to all connections neutral/ earth all correct.
A new pcb was fitted on Monday and the boiler fired immediately and all seemed well.
Monday night 8.30 pm ! phone call no heat/ hot water popped in and boiler had gone to over heat but I had left the boiler stat on max.
This morning 7.20 am phone call boiler gone to over heat again even tho stat was left on 3.
Same again tonight 5.30 pm boiler gone to overheat, even on no 1. I have checked the pump and it is running every thing in the apartment gets hot and works.
I am now told that during the down times the boiler had before I got involved the under floor heating (wet) was getting warm and the hot water was hot when they used the immersion heater, i presume it was picking up heat from the coil of the cylinder in a reverse fashion !!!
Sorry for the long post but they are neighbours and I am pulling my hair out !!!
next door has a problem with their Baxi Solo 3 60 pf.
Unbeknown to me other engineers have looked at the boiler, and I am now told they said it was the programmer but would not come back to replace.
New build block of apartments with underground parking, each having a boiler room with a baxi solo and unvented water cylinder, 1 heating zone for the bedrooms/ bathrooms another pump station for the under floor heating. Approx 8/9 years old.
I popped in last week and could not get the boiler to fire, correct voltage to all connections neutral/ earth all correct.
A new pcb was fitted on Monday and the boiler fired immediately and all seemed well.
Monday night 8.30 pm ! phone call no heat/ hot water popped in and boiler had gone to over heat but I had left the boiler stat on max.
This morning 7.20 am phone call boiler gone to over heat again even tho stat was left on 3.
Same again tonight 5.30 pm boiler gone to overheat, even on no 1. I have checked the pump and it is running every thing in the apartment gets hot and works.
I am now told that during the down times the boiler had before I got involved the under floor heating (wet) was getting warm and the hot water was hot when they used the immersion heater, i presume it was picking up heat from the coil of the cylinder in a reverse fashion !!!
Sorry for the long post but they are neighbours and I am pulling my hair out !!!