Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss betacom 30c, IT WORKS! in the Gaining Plumbing Experience area at Plumbers Forums

R

REDSAW

that surprised you. lol

Glow worm betacom 30c. keeps over pressurizing when heating is on then from 1&1/4bar rises to 3bar and blows prv. hot water works fine. exp vessel is 1&1/2 bar pump spins but return is cool? all rads heat up fairly quickly. cleaned return filter.
i set the stat on the boiler to low and seems to work at low rate ok but rads dont get too hot.
anyone got any pointers cause i'm scratching me head. thanks https://www.************/images/emoji.php/v6/f57/1/16/1f609.png
 
How big is system (rad count)
 
is there an old filling loop somewhere on the system which has started to let by

had one once, found an ancient filling loop in a cupboard where hot water cylinder had once been
 
is there an old filling loop somewhere on the system which has started to let by

had one once, found an ancient filling loop in a cupboard where hot water cylinder had once been
no, the pressure drops when heating not on, its got no where to expand or the pumps not strong enough as the return pipes cold. all rads warm up though ?????
 
Isnt there a filter on the return on these boilers? Maybe try cleaning that. Drop expansion vessel to 0.75-1bar
 
Your problem is most likely to be the expansion vessel.

It has either become defective or has lost its internal charge.

Turn off boiler and isolate flow and return under boiler.

Open boiler drain and leave open.

Attach a pump to the Schrader valve, pump out any water and
pump up vessel to about 0.7 - 0.9 bar.

If vessel OK then it should hold this charge.

Open flow and return and bring up pressure with filling loop to
1.1 - 1.5 bar.

You should find pressure now not shooting up and opening safety
valve.
 
nicely explained thanks,

pressure was 2bar and i dropped it to one and half seemed to work better!

i'll give that a go when i go back, should clear any blockage in the flexi pipe as well.
already cleaned the return filter.
 

Similar plumbing topics

  • Question
Problem found, it was a blockage... mostly in...
Replies
11
Views
1K
P
Mr Speaker: I'm tempted to draught a sarcastic...
Replies
22
Views
4K
Any update?
Replies
21
Views
2K
Deleted member 123817
D
  • Locked
You need a gas engineer to check the integrity...
Replies
8
Views
3K
If you cannot set temperature on the boiler...
Replies
3
Views
16K
GerryS
G
Back
Top