Biasi M90E no DHW or CH | UK Plumbers Forums | Plumbers Forums

Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

Discuss Biasi M90E no DHW or CH in the UK Plumbers Forums area at Plumbers Forums

PDS

Messages
19
Hi Guys, called out to a Biasi M90 with no DHW or CH. ignition pcb was faulty but since realised that there is no live to that board. I have a live feed into the main board and fuse is good. Do we reckon it’s the main pcb that’s at fault?
 
Overheat stat fine ?
 
Pump running when demand or just totally dead?
 
No voltage to fan ?

Check the pump proving circuit
 
as shaun said is spindle coming out on pump proving and operating the microswitch assembly on the left hand side of the boiler. if you take microswitch off its housing by removing the spring clip then turn on so pump running then push a small screwdriver into the hole to operate the m/switch and boiler fires up you need to change the diaphragm on pump proving assembly
 