Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Boiler adjustment after baffles cleaned in the Boilers area at Plumbers Forums

Messages
42
I've been told that after cleaning out baffles you can't analyse the gass accurately for some reason. Is there any truth in this?
Seems to me that if cleaned as thoroughly as possible the readings shouldould be more accurate than what they were when all sorted up inside. 🤔

Any pointers or advice on the matter hugely appreciated.

Thanks
 
You wouldn't stick your flue gas analyser into a sooted up boiler or flue. Whoever told you that is wrong. Once the boiler has been cleaned you would obviously then use your smoke pump before taking flue gas readings with your analyser to set the burner up properly.
If the person who told you that is also the person maintaining your boiler I would look at getting someone else.
 
🐂 --it cleaning baffles is part of a full strip down and service on a oil boiler, a new oil filter and nozzle is the norm and once completed the boiler is tested with a smoke pump with a temporary oil pressure gauge fitted , before finally using a flue gas analyser to achieve a satisfactory reading by either adjusting the air into the burner and or oil pressure . Kop
 
Thank you guys very much for the responses.
That's cleared that up nicely.

Of all the services the boiler has had over the years never have I seen anyone use a smoke pump. 🤔
I think I understand the idea of smoke test but can't quite see why it's an important step if a gas analyser is used afterwards.
Is it a visual aid to show customer or is it healthier for analyser to be closer to the correct setting or?

Im really interested to learn so very grateful for any further comments on this.
Thank you very much. 👍
 
Thank you guys very much for the responses.
That's cleared that up nicely.

Of all the services the boiler has had over the years never have I seen anyone use a smoke pump. 🤔
I think I understand the idea of smoke test but can't quite see why it's an important step if a gas analyser is used afterwards.
Is it a visual aid to show customer or is it healthier for analyser to be closer to the correct setting or?

Im really interested to learn so very grateful for any further comments on this.
Thank you very much. 👍
Healthier for the analyser as you say you really don't want to put it into a boiler with poor combustion it knacker the cells . Kop
 

Similar plumbing topics

Any gas boiler's HEX can stand a static head...
Replies
16
Views
1K
S
Boiler Fault I’m hoping someone can help with...
Replies
0
Views
116
S
    • Informative
Worcester normally have a section in the...
Replies
14
Views
7K
Have you cleaned the heat ex?
Replies
10
Views
2K
W
pcb issue so gas safe engy required sorry to say
Replies
1
Views
703
Back
Top