Old conventional non condensing combi boiler. Worcester 24i rsf.
Bungalow (ceiling drop pipes) with 7 rads.
I've bled rads.
Attempted to balance - Got them heating up at similar times now.
Boiler manual states 11 degree delta flow and return. Boiler is set to about 3/4 of max temp.
On the rads, not a problem - I can get 30c delta or just a couple of degrees easily- lots of adjustability on the lockshields.
I see about 60 degrees measured at rad flow and 50 at rad returns. But can adjust to less if necessary easily.
However........ the thermometers I have on the boiler flow and return never seem to go above 50 flow and 23 return. This seems wayyyy to low for a conventional non condensing boiler no?
I have read that such low flow and return to this type of boiler (specifically return) will lead to corrosion of the heat exchanger......as this non condensing boiler will be condensing and the chemicals given off in the flue fall back down and corrode the exchanger....
so how do I increase the boiler flow and return temps? Reduce lockshields further on the rads so the rads aren't giving away so much heat from the system or something else?
...
Old conventional non condensing combi boiler. Worcester 24i rsf.
Bungalow (ceiling drop pipes) with 7 rads.
I've bled rads.
Attempted to balance - Got them heating up at similar times now.
Boiler manual states 11 degree delta flow and return. Boiler is set to about 3/4 of max temp.
On the rads, not a problem - I can get 30c delta or just a couple of degrees easily- lots of adjustability on the lockshields.
I see about 60 degrees measured at rad flow and 50 at rad returns. But can adjust to less if necessary easily.
However........ the thermometers I have on the boiler flow and return never seem to go above 50 flow and 23 return. This seems wayyyy to low for a conventional non condensing boiler no?
I have read that such low flow and return to this type of boiler (specifically return) will lead to corrosion of the heat exchanger......as this non condensing boiler will be condensing and the chemicals given off in the flue fall back down and corrode the exchanger....
so how do I increase the boiler flow and return temps? Reduce lockshields further on the rads so the rads aren't giving away so much heat from the system or something else?