Hi everyone,

New here & my first post!

I have a Worcester greenstar 24i, it is a conventional boiler, it has a water tank upstairs.

For the past year the hot water when turned on was intermittent. I repressurised the expansion vessel to 1 bar and the hot water switch when turned on worked as it should, however the pressure upstairs was lower than usual, and not hot upstairs, rather it was warm (downstairs pressure and heat fine).

Upstairs, the showers also are not heating correctly and always cuts off. Unable to have baths as water is only luke warm.

Now the hot water switch is playing up again. The hot water only turns on when I wiggle this switch located near the water tank (see attached).

To summarise, 2 problems:

1: reduced pressure and hot water upstairs, showers not working as they should

2: hot water only turns on when I wiggle this switch (attached)

Please help, can't afford to repair or replace, but at least if I know the problem can try myself.

Many thanks
 

Attachments

  • 20230623_090533.jpg
    20230623_090533.jpg
    129.8 KB · Views: 55
  • 20230623_090318.jpg
    20230623_090318.jpg
    287.8 KB · Views: 45
It might be the motor inside that valve actuator or the microswitch. As for reduced pressure upstairs, has this always been an issue or a more recent thing? Check the cold water storage cistern is filling back up.
 
The cover would need to be removed warning - doing so exposes live conductors, proceed with caution.

Then check if the motor or switch, plenty of YouTube videos for a better understanding. The motor needs to motor all the way across to make the microswitch. As a newbie, you goth be best replacing the head without draining down if possible
 
Hi so quick update. There's no way to check the cistern on our water tank as it is sealed. I did purge the tank by emptying it completely, this has improved pressure slightly but not fixed the hot water issues upstairs. As for the valve, it looks like it needs replacing. Any other suggestions please on hot water upstairs?
 
Update, replaced the motor of the valve think it was called a synchronous, that's fixed the hot water not turning on, thanks for that! I haven't been able to fix the poor pressure, both my showers are cold unless I turn to max heat, bath is never warm enough. Attached is a photo of my cistern. Thanks
 

Attachments

  • 20230818_123230.jpg
    20230818_123230.jpg
    240 KB · Views: 39
  • 20230818_123235.jpg
    20230818_123235.jpg
    275.4 KB · Views: 37
Unvented cylinder tank stat should read 65c
 
There’s a square box 1/3 up from the floor
 
I don't think mine has a stat please let me know what you think.
 

Attachments

  • 20230820_122837.jpg
    20230820_122837.jpg
    257.6 KB · Views: 34
  • 20230820_122841.jpg
    20230820_122841.jpg
    235.8 KB · Views: 38
  • 20230820_122845.jpg
    20230820_122845.jpg
    240.7 KB · Views: 37
  • 20230820_122848.jpg
    20230820_122848.jpg
    213.8 KB · Views: 36
  • 20230820_122854.jpg
    20230820_122854.jpg
    267.8 KB · Views: 36
  • 20230820_122900.jpg
    20230820_122900.jpg
    274 KB · Views: 36
  • 20230818_123235.jpg
    20230818_123235.jpg
    275.4 KB · Views: 36
In the unvented hot water panel you see the stickers on it so doubt it’s been knocked so that’s no the issue

But you have a tmv3 on your hot water out for some reason eg follow the top pipe out of the cylinder you will see 2 other pipes link to that with a chrome valve

Do you know why that’s on it ?
 
Update, replaced the motor of the valve think it was called a synchronous, that's fixed the hot water not turning on, thanks for that! I haven't been able to fix the poor pressure, both my showers are cold unless I turn to max heat, bath is never warm enough. Attached is a photo of my cistern. Thanks
That’s a photo of the cylinder, not the cistern
 
In the unvented hot water panel you see the stickers on it so doubt it’s been knocked so that’s no the issue

But you have a tmv3 on your hot water out for some reason eg follow the top pipe out of the cylinder you will see 2 other pipes link to that with a chrome valve

Do you know why that’s on it ?

I have absolutely no idea, it's been like that since I moved in 2009.
 
No problem at all! Is there a valve that could be stuck or anything in particular I should check for the lack of pressure?
I don’t hold my G3 quali’s, but assuming the cold main is still ok, maybe the pressure reducing valve, or blending valve - but these would need a G3 registered engineer.
 

Similar plumbing topics

L
That shouldn't happen. Going to need lots of...
Replies
1
Views
296
Hi we’re the boiler sited
Replies
7
Views
912
B
No the installers need to come out
Replies
10
Views
2K
T
Please advise me. I am a disabled pensioner. I...
  • TheCatWhoNeedsaHotShower
  • Boilers
  • 0
  • 471
  • Latest:
  • TheCatWhoNeedsaHotShower
Replies
0
Views
471
TheCatWhoNeedsaHotShower
T
the op says no water in prv balloon so not prv...
Replies
7
Views
1K
Back
Top