Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Boiler Losing Pressure in the Boilers area at Plumbers Forums

Status
Not open for further replies.
Messages
10
Hi,

My Vaillant Turbo Compact is losing pressure. It drops about 0.1 bar per week.

I have ruled out the boiler (engineer checked it: expansion vessel, pressure relief valve, etc) so it may be a leak.

I have checked all visible joints around rads and all ok. It may be a leak under floorboards. The pipes have copper compression fittings.

Does anyone have any good ideas for finding small leaks? I live in a flat and the neighbour downstairs does not have any problems with leaks in ceiling.

Thanks
Mac
 
Hi Mac,
Somehow I feel like every new member rights and ask about the same thing so don’t get me wrong it’s just weird.


Either get a good engineer around or use perhaps thermal imaging camera.
 
As it's such a small amount you could try some leak sealer
 
Confirm its not your expansion vessel or PRV by tying a sandwich bag or similar onto the warning pipe outside to catch any water should it let by, not saying there anything wrong with your engineer but you would be surprised how little understanding some engineers have of EV's, did he drain down before checking the air pressure? Is it a condencing model?
 
Status
Not open for further replies.

Similar plumbing topics

thank you, good tip, I will try
Replies
3
Views
1K
the op says no water in prv balloon so not prv...
Replies
7
Views
1K
Ok great...really hoping it wasn't a leak.
Replies
6
Views
640
That means you have a leak as the system...
Replies
9
Views
820
M
Isolate and drain boiler. Pump up expansion...