Hi,
Not sure if this is the place to post this, but hope some one can help.
My Central Heating water temperatures seem to fluctuate a lot, while I’m using a modulated system. Within an hour is goes from 50 degrees to 20 degrees many times, while the outside temp as wel as the room temp remain stable during this time.
Is a modulating system supposed to work like this?
In other words: Should it not level out and become stable after a while if the room/outside temperatures are not changing?
Details:
Using Open Therm I collect various info among which is the Boiler setpoint temperatures and CH water temperatures.
I'm using a weather compensation control setup and I can see the Boiler CH Setpoint temperatures nicely being set and following (opposite temp curve) the outside temperatures. I.e. the lower the outside temp's get, the higher the CH setpoint on the boiler is. So far so good.
When I then look at the actual measured CH water temperatures (using remote temperature sensors), I see that the temperature constantly fluctuates strongly and totally unlike the Setpoint. It seems to act much more like a on/off switched boiler, rather than a nicely modulated system.
To be sure I checked the CH return temperatures not rising to high and the power is maximized.
Can anyone explain why I do not see a much more stable CH water temperatures. The systems does not look efficient this way.
System used:
Boiler: Remeha Tzerra Ace 36 (year: 2022)
Nefit Easy room thermostat (using Opentherm gateway)
Not sure if this is the place to post this, but hope some one can help.
My Central Heating water temperatures seem to fluctuate a lot, while I’m using a modulated system. Within an hour is goes from 50 degrees to 20 degrees many times, while the outside temp as wel as the room temp remain stable during this time.
Is a modulating system supposed to work like this?
In other words: Should it not level out and become stable after a while if the room/outside temperatures are not changing?
Details:
Using Open Therm I collect various info among which is the Boiler setpoint temperatures and CH water temperatures.
I'm using a weather compensation control setup and I can see the Boiler CH Setpoint temperatures nicely being set and following (opposite temp curve) the outside temperatures. I.e. the lower the outside temp's get, the higher the CH setpoint on the boiler is. So far so good.
When I then look at the actual measured CH water temperatures (using remote temperature sensors), I see that the temperature constantly fluctuates strongly and totally unlike the Setpoint. It seems to act much more like a on/off switched boiler, rather than a nicely modulated system.
To be sure I checked the CH return temperatures not rising to high and the power is maximized.
Can anyone explain why I do not see a much more stable CH water temperatures. The systems does not look efficient this way.
System used:
Boiler: Remeha Tzerra Ace 36 (year: 2022)
Nefit Easy room thermostat (using Opentherm gateway)