Hi,
I have a Grant combi and the PRV is passing and constantly dripping hot water. The boiler pressure is around 2.2bar, which is close to the 2.5bar PRV setting.
I firstly vented the pressure down to 1.2 bar and it rose back up in less than an hour.
I checked the expansion tank and there was water on the air side so I then replaced the expansion tank. Problem still exists.
I disconnected the fill loop completely in case that was passing. Problem still exists.
I must have vented the system about 10 times over the last couple of weeks so there is pressure coming from 'somewhere' and since the fill loop is gone then the only thing I can think of is the heat exhanger. Do these tend to fail and allow water to pass to the heating loop? Can they be replaced by a competent DIYer?
This is a Grant Vortex 26e combi. Thanks!
I have a Grant combi and the PRV is passing and constantly dripping hot water. The boiler pressure is around 2.2bar, which is close to the 2.5bar PRV setting.
I firstly vented the pressure down to 1.2 bar and it rose back up in less than an hour.
I checked the expansion tank and there was water on the air side so I then replaced the expansion tank. Problem still exists.
I disconnected the fill loop completely in case that was passing. Problem still exists.
I must have vented the system about 10 times over the last couple of weeks so there is pressure coming from 'somewhere' and since the fill loop is gone then the only thing I can think of is the heat exhanger. Do these tend to fail and allow water to pass to the heating loop? Can they be replaced by a competent DIYer?