Hello everyone,
I have a Vaillant Ecotec Plus 838. The issue i have is after the heating is switched on and then left it to cool over night i see the pressure has gone up.
For example yesterday it was set at 1.3 heating was switched on and when it reached its temp it went upto 1.9 so no issues. But when its left to cool over night the pressure shows 1.8 in the morning. The pressure in the expansion vessel was at 1.0 bar and when checked this morning its at 1.5 bar. The expansion vessel was replaced yesterday.
I have been monitoring this for weeks and everyday letting the pressure out.
Why is the air pressure in the expansion vessel going up ? is there another part to replace?
If you require any info from the boiler please let me know and I will get them for you.
Not technical at all with these things so please be gentle when replying. 🙂
I have a Vaillant Ecotec Plus 838. The issue i have is after the heating is switched on and then left it to cool over night i see the pressure has gone up.
For example yesterday it was set at 1.3 heating was switched on and when it reached its temp it went upto 1.9 so no issues. But when its left to cool over night the pressure shows 1.8 in the morning. The pressure in the expansion vessel was at 1.0 bar and when checked this morning its at 1.5 bar. The expansion vessel was replaced yesterday.