Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Boiler won’t fire on H/W in the Boilers area at Plumbers Forums

Status
Not open for further replies.

stratplus

Plumbers Arms member
Plumber
Gas Engineer
Messages
953
Vaillant Turbomax VUW 242E.
Fires fine on heating, turn on hot tap and burner goes out.
So it’s recognising there’s s call for h/w.
Could this be the diverter valve or more likely the micro switch?
Hot water is achieved with heating on apparently. Anyway to check the diverter on this boiler?
 
Vaillant Turbomax VUW 242E.
Fires fine on heating, turn on hot tap and burner goes out.
So it’s recognising there’s s call for h/w.
Could this be the diverter valve or more likely the micro switch?
Hot water is achieved with heating on apparently. Anyway to check the diverter on this boiler?
Anyone?
 
No heating on turn the hot water on does it start ?
 
I would say flow sensor if it has one
 
I would say flow sensor if it has one
Not sure this boiler has one. MI’s mention micro switch not being activated? Strange that when heating is on a call for hot water cuts out the burner. Yet on h/w only nothing happens. Can’t call tech until tomorrow.
 
So it's like the mains /baxi pin comes out ?

You manually pressed the micro switch with a hot tap open ?
 
So it's like the mains /baxi pin comes out ?

You manually pressed the micro switch with a hot tap open ?
Not sure Shaun, just about to print the manual to have a good look. Diaphragm diverter by the look of it.
Gets h/w when heating has been on....or has done up until recently apparently. Had this problem for a while.
 
You can still buy the water section for it and replace it. You will be able to see the diverter valve lift when you open a tap. It s on the right hand side and it has a micro switch to the right of that
 
I would say diaphragm problem.

The micro switch is sits on the side of diverter valve.

You should be able to push the switch with a small screwdriver
and see if the burner fires.

 
As the guys have said a service kit is available for the diverter valve part number 140352 tricky to do if you havent done one and swap the hot water thermister part number 252805 at the same time . best of luck kop
 
As the guys have said a service kit is available for the diverter valve part number 140352 tricky to do if you havent done one and swap the hot water thermister part number 252805 at the same time . best of luck kop
Thank you KOP. Really helpful. Much appreciated.
 
Status
Not open for further replies.

Similar plumbing topics

S
Boiler Fault I’m hoping someone can help with...
Replies
0
Views
114
S
I don't believe moving the manual lever over...
Replies
5
Views
505
The two components that electrically turn on...
Replies
5
Views
1K
There is 6 pipes under the boiler and one goes...
Replies
19
Views
971
Back
Top