Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Boiler works ok on CH but goes to lockout when hw selected in the Boilers area at Plumbers Forums

Status
Not open for further replies.

armyash

Esteemed
Plumber
Gas Engineer
Subscribed
Messages
2,650
Hi guys

Just had a call from a customer, the central heating works fine but as soon as he turns off the ch and selects hw, the boiler locks out and requires a reset.

Any ideas? I am unable to get there until tomorrow evening.

It's S or Y plan, could it be a faulty bypass, div valve or no pump over run??

Just a couple of ideas. Baxi Solo 380 PF
 
Last edited:
2 port or 3 port not opening would be my first port of call buddy.
 
no circulation, boiler over heating. check gate/ balancing valve is open on coil before anything else.
 
Gate valve on coil pipe is open but looks worse for wear, said i will change that.

With CH off at programmer, rads still get hot when just on hot water. Motorised valve does not seem to be working as i switch between the hw and ch.

When just on HW the pump makes a bit of a racket and the vent pipe gets hot, if i stop the pump then start it again i can hear water shooting out of vent pipe and the pipe cools down.

CH seemed to be working fine.
 
It's a circulation issue. If all valves are opening correctly then possible blocked coil. This may be an instance where the Bg favoured PF is actually needed.
 
Status
Not open for further replies.

Similar plumbing topics

    • Like
Great summary and well done for getting it...
Replies
1
Views
2K
Its easy to check for a leak, just tie up the...
Replies
7
Views
1K
Which model combi? Have you checked heating...
Replies
1
Views
761
Back
Top