Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Boilermate 2000 in the Boilers area at Plumbers Forums

Status
Not open for further replies.

E4gas

Plumbers Arms member
Plumber
Gas Engineer
Messages
564
Heating comes on when room stat off , demand for hot water only.
Heating travering up the return , change non return valves on pumps
 
If heating pump runs when, hw tap is opened then aplliance control board has to be duff.
 
Changed that months ago ,as soon as you turn on b/m heat travels to nearest rad . No pumps on
 
Agree that I would be double checking the board, and that the correct inserts in the board had been fitted.

Then I'd look at the programmer and then the board on the boiler.

One of the pumps has to be running.
 
Thanks I double check , pcb is easy to change , more concerned about reverse heat
 
double check the htg pump is not running when the rads are heating up.
 
Status
Not open for further replies.

Similar plumbing topics

You’re 200 miles away - he is there. You’re...
Replies
3
Views
606
S
Boiler Fault I’m hoping someone can help with...
Replies
0
Views
132
S
200% won’t be the reason the cylinder isn’t...
Replies
10
Views
1K
Hi all, Just looking for some advice if...
Replies
0
Views
1K
A
Are you sure it’s still vented? Should have...
Replies
1
Views
1K
Deleted member 120897
D
Back
Top