Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Boiling Water in F&E Tank in the Boilers area at Plumbers Forums

Status
Not open for further replies.
W

wild nomad

Hi There,

A customer has an F&E tank that is practically turning into a kettle when the heating comes on. She also has complained that the hot water is scolding! Other than a dodgy boiler thermostat, does anyone have any ideas what could be causing this?

Thanks in advance :)
 
is it pumping over?

how hot is the water?
how long is it set to be on?
immersion heater left on 24/7?

more investigation required.
 
is it pumping over?

how hot is the water?
how long is it set to be on?
immersion heater left on 24/7?

more investigation required.


is it pumping over?

how hot is the water?
how long is it set to be on?
immersion heater left on 24/7?

more investigation required.


Haven't been around to look yet I just wanted to go armed with some ideas as I can't touch the boiler as I'm not Gas Safe yet. Can't say how hot the water is but apparently the last engineer said it had warped the first 6 inches of the overflow pipe as it exited the F&E tank. So pretty damn hot! No immersion heater. The heating is working fine so no air locks below the highest rad and they haven't complained about rads coming on when the heating is off so I'm assuming the port valve is OK.

They have recently had their F&E and CWSC replaced about 3 months ago and apparently problems started about 3 or 4 weeks after the install. When I fitted a shower there I looked at the new water tanks installation and it looked fine to me. All up to building regs. Will check to see if it's pumping over when I get there.

Cheers for the ideas!
 
It will be down to the configuration of the feed and vent, where they are connected in. And pump position.
For a quick fix, try extending the vent as high as possible. Drain some water out of the f&e tank and lower the water level Dow to about 1/4 of the tank depth.
if this doesn't work, a bit more investigation is needed.
 
If its getting that hot it needs sorting pretty quick B4 someone gets scalded
 
Status
Not open for further replies.

Similar plumbing topics

B
No the installers need to come out