Kewat66
Gas Engineer
- Messages
- 119
Hi All,
i have been working on a British Gas 532i ( Worcester with BG badge )
boiler kept losing pressure. Checked the pressure in the vessel and noting showing so re-pressurised to 1 bar. Called back next day as pressure dropped to zero on gauge. So I changed the vessel & prv. Refilled system to just over 1 bar and boiler went into the venting mode. Waited for 45mins and all worked fine.
an hour later I get a call saying pressure has gone down to .5 bar but all still working. What I did notice On filling the boiler the gauge wouldn't go past 1.5 bar but you could here the water going in still.
could this be a faulty gauge showing 1.2 bar but really be over full and dumping the water?
thanks
kevin
i have been working on a British Gas 532i ( Worcester with BG badge )
boiler kept losing pressure. Checked the pressure in the vessel and noting showing so re-pressurised to 1 bar. Called back next day as pressure dropped to zero on gauge. So I changed the vessel & prv. Refilled system to just over 1 bar and boiler went into the venting mode. Waited for 45mins and all worked fine.