Hi all,
I have an interesting fault with this boiler.
DHW running fine until the boiler "thinks" it's too hot and somehow dumps the contents of DHW into the CH loop,nswitches off the burners and restarts the ignition sequence as per normal.
DHW runs cold for a short while until returning to temperature.
This happens whether CH is on or off.
All thermistors are will within tolerance
Water flow rate is around 9-10 Litres/min at the HW tap-end
Fan up to speed and Air pressure switch working fine.
This continues ad infinitum... Unless the DHW temp control is set to minimum. Anything above min, say 25% plus, the fault manifests itself again.
Needless to say, the pressure in the CH system constantly reaches to a point where the PRV releases water via the runaway. There seem to be no other leaks into the CH.
Increasing the incoming water flow reduces this problem somewhat, so that the time it takes to dump water into the CH loop is extended. Of course the water temp will be a little lower due to the increased rate of flow.
Is there some invisible diverter/dump valve that I seem to have missed or some unique function of the HX? Or a faulty HX, even?
Kindest regards and TIA.
I have an interesting fault with this boiler.
DHW running fine until the boiler "thinks" it's too hot and somehow dumps the contents of DHW into the CH loop,nswitches off the burners and restarts the ignition sequence as per normal.
DHW runs cold for a short while until returning to temperature.
This happens whether CH is on or off.
All thermistors are will within tolerance
Water flow rate is around 9-10 Litres/min at the HW tap-end
Fan up to speed and Air pressure switch working fine.
This continues ad infinitum... Unless the DHW temp control is set to minimum. Anything above min, say 25% plus, the fault manifests itself again.
Needless to say, the pressure in the CH system constantly reaches to a point where the PRV releases water via the runaway. There seem to be no other leaks into the CH.
Increasing the incoming water flow reduces this problem somewhat, so that the time it takes to dump water into the CH loop is extended. Of course the water temp will be a little lower due to the increased rate of flow.
Is there some invisible diverter/dump valve that I seem to have missed or some unique function of the HX? Or a faulty HX, even?
Kindest regards and TIA.