B
buckley plumb
been to this today and phoned Worcester tech who were not much help. boiler fires and flame on for 1 min during this time the sparker is still sparking every 10 seconds then repeats the process .checked continuity from end of probe to board so cable is ok.removed cable from probe and put meter on micro amps and tested - with gas off and boiler turned on got 1micro amp which didn't change when sparking (was expecting 5ma min) .but when gas was turned on and the boiler fired and flame on got 9micro amps. spoke 2 tech twice 1st time I was told I should get 14micro amps and its the probe . 2nd time told I should get 5 micro amps when sparking.by this time my head is spinning -leave job and manage to call a Worcester engineer who seemed to think I wouldn't get a micro amp reading while its sparking but would once its lit.anyone got any advice on these boilers . a weird thing I noticed was with the combustion cover on the boiler sparked and fired for 1 min sparking every 10 sec but when removed the boiler sparked but no gas but then removed the insulation cover and it sparked and lit for 1 min sparking every 10 sec. I am thinking board .