Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss BS 1212 Part 2 Air gap in the Air Sourced Heat Pumps area at Plumbers Forums

Messages
65
Hi
Am unable to find a clear answer to this -

But the water in the cistern with BS 1212 part 2 float valve what is the highest water category that it can be?

Im thinking category 3 has in F and E tank not been able to find anything written in WRAS guidebook.

Can anyone clarify this?
Thanks!
 
Cat 5 if you drill the holes to spec
 
Hi thanks so far but just normal tank with 1212 part 2 valve With out adding extra weir holes into it.

Correct only thing overflow must be sized correctly and terminate to outside

If into stack / waste pipe needs to have an air gap

Weir holes is an AA air gap

IMG_3651.PNG
 
What you planning on doing that's cat 5 risk ?
 
The rainwater harvesting set ups are generally cat 5 due to potential for bacteria etc so yes you would be correct to assume the pigeon faeces would be a cat 5 risk, therefore a suitable back flow prevention set up would be required to provide the appropriate backflow protection against the risk described suirable AB. AA air gaps etc pipe id
 
The use of a BS1212 part 2 float valve does in its self guarantee the air gap it just helps with the amount of water that can be stored & still maintain the air gap.
It always down to the Plumber to drill the holes in the right places to achieve this, air gaps are dependant on the size of the inlet & overflow.
 
Correct only thing overflow must be sized correctly and terminate to outside

If into stack / waste pipe needs to have an air gap

Weir holes is an AA air gap

View attachment 33924
Sorry Shaun but a weir overflow is an AB.
AA is where inlet is above the cistern overspill & free falls into the cistern. Both however are good for Cat 5 & are the only ones that should be used for a rainwater storage if that is what the OP is doing.
ref - WRAS book 6.13
 

Similar plumbing topics

O
  • Article
Are at home Level 2 courses actually viable...
Replies
0
Views
142
OLG0824
O
I think its a room stat per UFH room zone
Replies
2
Views
733
O
  • Article
Any experience with Optima Electrical Training...
Replies
0
Views
149
OLG0824
O
J
  • Article
gate intercom / gate openers can anyone...
Replies
0
Views
118
James
J
  • Article
Shower tray not flush to wall Hello All, I...
Replies
0
Views
119
Back
Top