pmac10
hi, im an industrial elec/mech maintenance engineer and was called to my parents house as their burner went to lockout after failing to cycle. the pump is the problem as the motor metered fine as did the capacitor and the fan is free to rotate. i decoupled the pump from the motor and it has tight spots.
problem. i have a new pump to fit but do not have the tools to set the pump pressure, do a smoke test or carry out flue gas anylasis (i have a piece of paper with oftec 101 cert on it) but not even a smoke pump to put it in.
this is an off the shelf danfoss bfp 21 pump. any thoughts on the way forward. im not commissioning a new pressure jet appliance, just fitting a new pump to an existing one.
any advice greatly recieved