Hi,
My central heating has been bad for many years now (several radiators not heating up) and I've only just found that the gate valve in the bypass circuit is fully open - water can flow around through the pump and back to the boiler without going through any radiators.
Shutting the valve completely means all the radiators heat up in seconds.
However due to the way it's been set up, when only the hot water is on (and heating is off) it has to flow through this bypass valve to return to the boiler. So it needs to be open.
What is the best practice for setting the amount this valve is open? Should it actually be fully open or do I need to find a balance?
I also see you can get automatic valves. Would it be beneficial to get one?
This is a regular boiler system around 20 years old.
My central heating has been bad for many years now (several radiators not heating up) and I've only just found that the gate valve in the bypass circuit is fully open - water can flow around through the pump and back to the boiler without going through any radiators.
Shutting the valve completely means all the radiators heat up in seconds.
However due to the way it's been set up, when only the hot water is on (and heating is off) it has to flow through this bypass valve to return to the boiler. So it needs to be open.
What is the best practice for setting the amount this valve is open? Should it actually be fully open or do I need to find a balance?
I also see you can get automatic valves. Would it be beneficial to get one?
This is a regular boiler system around 20 years old.
Last edited: