Charge it to 0.1 or 0.2 bar greater than the Pressure Reducing Valve, Mas
You can't use the static pressure as it fluctuates you could set it up for a 10M head to find that at night when the Economy 7 is on & water is heating the mains is at 20 or 30Metre.
Think about it, you want the bladder held flat with the air pressure when cold, only allowing water in as the pressure in the system starts to rise as it heats, thereby creating more volume in the system when hot that when cold = controlling pressure rise.