Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Can I remove a radiator off the wall if the thermastat is broken in the UK Plumbers Forums area at Plumbers Forums

Messages
2
We have a plasterer coming this week and the radiators need to come off! A DIY friend came round and removed all but 1 radiator as he wasnt sure what to do as the thermastat on one end has been broken??? HELP if we turn the valve off at the other end will this do the job so we can just remove it OR do we have to replace the thermastat on order to then turn it off both ends? Blind leading the blind and running out of money! First pic we think had a thermastat on!
 

Attachments

  • 20191117_191705.jpg
    20191117_191705.jpg
    80 KB · Views: 34
  • 20191117_191711.jpg
    20191117_191711.jpg
    44.4 KB · Views: 35
HELP if we turn the valve off at the other end will this do the job so we can just remove it
No.
do we have to replace the thermastat on order to then turn it off both ends?
If it's what it looks like, i.e. a broken TRV, so you can't shut it reliably then yes.

You'll need to drain down the system to be able to remove the radiator and replace the broken valve. There are techniques (freezing, bunging, etc.) that can be used to avoid draining down but they take practice to get right and are best left to professionals.

If you drain the system, make sure you put the correct amount of inhibitor back when you refill it.
 
Is it the old type with a screw in it to tighten it on to the valve? Might need a nip up if it is.
[automerge]1574067252[/automerge]
Never mind. Just blew the pic up and it looks snapped. Sorry
 
Last edited:
No.

If it's what it looks like, i.e. a broken TRV, so you can't shut it reliably then yes.

You'll need to drain down the system to be able to remove the radiator and replace the broken valve. There are techniques (freezing, bunging, etc.) that can be used to avoid draining down but they take practice to get right and are best left to professionals.

If you drain the system, make sure you put the correct amount of inhibitor back when you refill it.
Your trvs came with a manual over ride just for this purpose you should use this. NEVER rely on
just closing the trv as the lowest they go is frost...so when the room gets cold the valve will open
up and flood the room. seen this loads of times. centralheatking
 
Your trvs came with a manual over ride just for this purpose you should use this. NEVER rely on
just closing the trv as the lowest they go is frost...so when the room gets cold the valve will open
up and flood the room. seen this loads of times. centralheatking

Good advice, however for a good few years now TRVs close right down passed the frost setting all the way to 0 (fully closed, no frost opening possible) but it's still necessary to add appropriate caps to the valves in case of let-by failure.

Not saying you are wrong as there are loads of the older style you mention so better safe than sorry, just thought I'd add that for clarity.

Those manual override caps AKA "Decorator's caps."
 

Similar plumbing topics

  • Question
These
Replies
11
Views
2K
  • Question
Those LCD panels look spot on and better than...
Replies
5
Views
819
  • Question
Oh nice one, that's really useful. Those look...
Replies
6
Views
1K
  • Question
Assuming you have a Greenstar i 24 system...
Replies
5
Views
922
D
  • Question
Basin waste will be 1 1/4” whereas you want 1...
Replies
2
Views
572
Back
Top