Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Can't get all rads working on new system in the Gaining Plumbing Experience area at Plumbers Forums

KingDoey

Plumbers Arms member
Plumber
Gas Engineer
Messages
288
Good evening all.

Last job today to repair a leak on a brand new heating system. Is a combi boiler.

Drained down. Repaired leak and refilled. Vented and ran system. On 5 of 8 rads getting hot. Tried balancing system and no better. Ran boiler on max. Still 3 stone cold rads.

EngIneer before me says system was running hot all round before leak. Any ideas why 3 rads stone cold. Have removed all air from system. Set boiler on purge programme several times. Just can't get it to circulate.

Even with every radiator off bar the three cold ones the boiler just cuts off.

Any ideas?
 
Moved some rubbish about blocking those 3 ??
 
Thanks chaps

Yeah the guy who had it running before said it was defo working like a dream. I trust him aswell as I know him.

Shaun I thought a blockage, yet the 3 radiators affected are at different stages of the run if that makes sense. They are in between hot radiators.

I am literally stumped....
 
I would pull the rads and see if you have flow then both valves but won't be quick

Trv pins arnt stuck ??
 
Tell us where the 3 cold radiators are and about the path the pipes to/from them take.

Could they be on a separate zone with a zone valve hidden somewhere non-obvious?

Are you sure the pump is running and pumping effectively, could the 5 hot ones be being kept warm by gravity circulation (unlikely with a modern boiler) or a weak pump that is on the way out?
 
Shut the valves off to the rads let the pressure off take out the plug opposite the manual air vent and pipe up to a hosepipe run to a drain open up trv and filling loop and flush through do this on the 3 rads and refill and vent, see if this improves the situation . cheers kop
 
Turns out the apprentice had messed about with the lockshields. Didn't even think to check them since 2 hours before the other engineer had the system hot. Funny how you overlook the simple things!

Cheers for all the advice!
 

Similar plumbing topics

With CH selected on, if you open a hot tap...
Replies
2
Views
547
You seem to have got it sorted, but for future...
Replies
7
Views
944
Thanks :) . A happy new year to you!
Replies
23
Views
1K
Can't remember if you can get the UFH working...
Replies
18
Views
2K
  • Question
It could well be, the OP will soon hopefully...
2
Replies
35
Views
2K
Back
Top