Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Cascading 2 boilers in the Boilers area at Plumbers Forums

Status
Not open for further replies.
M

mike_s

How was this done the old fashioned way?

I ask because I have a customer who has 2 heat only boilers, pressurised with external expansion vessell etc.

The system is between 5 and 10 years old, there are 4 non-return valves in total, one for each flow and return.

They have a problem with one boiler overheating when the other is on, boiler stat and over heat cut off seem to be working fine.

The pump is on the return, working and overunning fine however I'm going to move the pump to the flow, before the 3 zone valves (s plan plus system) as I'm thinking the non-return valves are preventing the heat escaping as the pump is incorrectly positioned.

Failling that, I will check out the non-return valves.

Does this sound about right? I've spoke to various manufacturers and these days they insist on low-level headers but the non-return valve method was the old school way so how should this be done?
 
never seen it done with non return valves ive done a fair few over the years and just linked them into suitably sized pipework with iso valves to allow repairs etc to either boiler the non return valves may indicate a previous problem i cant see how moving the pump will help is there a bypass to allow circulation on over run as s plan will shut flow completely?
is the pump wired from both boilers ?
if only one boiler is going to overheat have you tried running just that boiler see if it still happens if it does id be thinking boiler problem rather than system
 
To cascade them the old fashioned way. You set the thermostat 5-10 deg c lower

And then on annual service you alternate the lead and lag
 
Cheers guys, sorted it today, made up. We ended up taking off all 4 non-return valves and one was blocked solid, the others were falling apart, so we just joined the pipes back up without them and even just the one boiler managing to heat the 200 litre unvented cylinder and about 20 radiators, customer made up and says it's the best the system has ever worked.
 
I was going to say take a butcher's at the nrv's but you beat me to it! Low loss headers are the way to go though if you ever need to cascade a pair of boilers in the future.
 
cheers, he wants me to replace the boilers in a couple of years or when they break down and I'll probably go for Worcester RI's with a low less header, there's a technical bulletin on their site of how to do it and their technical services are great should I need any help designing the system.
 
you should have left the nrv on the flow pipes for each boiler, when one of the boilers (and pump) switchs off the other pump will push water back through the first boiler.
 
you should have left the nrv on the flow pipes for each boiler, when one of the boilers (and pump) switchs off the other pump will push water back through the first boiler.
there is only one pump so doesnt need nrv's there would be little heat loss through the boiler that wasnt firing
 
yep it is only one larger grundfos pump on 28mm pipework. I replaced the overheat cut off incase that was faulty too.
 
you only need low loss headers to cascade boilers with internal pumps usually a pair of sytem boilers
 
Status
Not open for further replies.

Similar plumbing topics

Thanks guys. Just finished and managed to set...
Replies
9
Views
2K
200% won’t be the reason the cylinder isn’t...
Replies
10
Views
1K
A
Are you sure it’s still vented? Should have...
Replies
1
Views
1K
Deleted member 120897
D
As long as your flow pipe is getting hot first...
Replies
5
Views
1K
Back
Top