Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Central Heating circulation issue in the Central Heating Forum area at Plumbers Forums

Messages
62
Hello i recently converted heating system from old stove to grand vortex b house 90 , boiler runs and works fine . How ever i have issue with water circulation have installed new pump but for some reason water don't circulate at all . what are the possible cause ? i have pump installed on return and and have one way valve on coil return I have attached image on how it looks like and schematics
20221011_1812082.jpg
Untitled-3.jpg
 
Pump installed in the wrong place also shouldn’t be facing up the bleed screw needs to be on the side or at worst 45 degrees
 
After the cylinder but your feed and vent arnt in the best position most likely will pump over
 

Attachments

  • A404CFD1-91D5-40F9-8ABD-452549EC40EA.jpeg
    A404CFD1-91D5-40F9-8ABD-452549EC40EA.jpeg
    52 KB · Views: 40
As per my image also best to upgrade to an s plan from a gravity set up also while your at it eg port valves
 
So in the picture the right are the pipes straight from the boiler ?
 
So the left out the floor is the boiler ones
The ones on the right are to your rads ?
 
Left hand side flow out the floor going upwards
Vent
Feed
Pump
Port valves for heating and hot water

If you want me to draw it out will knock something up tomorrow for you
 
Yes and basicaly feed and expension pipe are the same . So if i understand this correctly best possition for he pump is on the flow right after t junction on downwards pipe that goes into rads and expansion pipe than would push water down then ?
20221012_112351.jpg
 

Attachments

  • 20221012_112847.jpg
    20221012_112847.jpg
    374.9 KB · Views: 35
Last edited:
My 50 year old system has the exact same combined cold feed and vent but the pump is installed just before the (oil fired) boiler return on the ground floor.

A bit surprising, if the rad returns were into the pump suction that it wasnt circulating through the rads at least.
I think yes, install the pump on the flow side and ensure the cylinder flow and rads flow pipes are downstream of the pump discharge, assuming that you want to have a fully pumped CH&HW system. I would also suggest installing a 1/2" gate valve on the cold feed to the Feed&expansion tank ballcock filling line as you should fill the system very slowly so as the air can vent up through the same pipe that the water is filling the system through.
 
Last edited:
I have moved pump to different location it seems to be working noe all fine . But the problem doest really heat hot water very well qnd forst floor radoators as well . Both flow and return pipes are hot now all rads on second floor also hot but hot water cylinder and first floor rads cold or at least it takes way longer to heat them up .
20221012_140110.jpg
 
I see the pump is on Auto setting, you might change that to a higher setting and post the make/model of the pump, most pumps, Grundfos etc just don't work on this Auto setting. Also the cylinder coil NRV should be removed IMO (if still installed) especially if a spring loaded type but try pump on different setting for a start.
 
should be installed like this
 

Attachments

  • 1.png
    1.png
    12.7 KB · Views: 36
I see the pump is on Auto setting, you might change that to a higher setting and post the make/model of the pump, most pumps, Grundfos etc just don't work on this Auto setting. Also the cylinder coil NRV should be removed IMO (if still installed) especially if a spring loaded type but try pump on different setting for a start.
if i take off NRV then it stops circulating . i would guess i need to redo feed and pump location . Put pump on flow before boiler and feed before pump like in example ShaynCorbs send
 
I would think that it should work if you install in the horizontal pipe just above it and shift the vent to the left of it, that way the cold feed is to the suction side of the pump and the whole system should operate at a positive pressure. As installed IMO, should still work but not the best as system will be at negative pressure in places.
Ideally, should have mot.valve and balancing valve on cylinder coil as cylinder temp will run at the boiler temperature otherwise.
Shaun is showing the pump on the flow from the boiler, pump pumping away from the boiler (correctly), but the above mod should achieve the same IMO.

Have you changed the pump settings?.
 
I would think that it should work if you install in the horizontal pipe just above it and shift the vent to the left of it, that way the cold feed is to the suction side of the pump and the whole system should operate at a positive pressure. As installed IMO, should still work but not the best as system will be at negative pressure in places.
Ideally, should have mot.valve and balancing valve on cylinder coil as cylinder temp will run at the boiler temperature otherwise.
Shaun is showing the pump on the flow from the boiler, pump pumping away from the boiler (correctly), but the above mod shouachieve the same IMO.

Have you changed the pump settings?.
Yes i tried to set to max but as soon as i take out NRV its stops circulating or atleast ot doest pump hot water from boiler though the system .
 

Similar plumbing topics

Sometimes the connection point of the cylinder...
Replies
3
Views
552
Thermal store fits the bill but don’t forget...
Replies
1
Views
306
And loose efficiency
Replies
2
Views
1K
B
Context for issue: I'd like to start by...
Replies
0
Views
560
Butchy10
B
Can central heating / gas engineer expert help...
Replies
0
Views
823
Back
Top