A recent problem turned up with my central heating.
It is a classical gas open vented system: gas boiler, loft cistern, indirect hot water cylinder, cylinder thermostat, living room thermostat, controller with separate knobs for hw and ch.
Symptoms:
1) if HW is off, nothing happens (irrespective of the thermostat setting and/or the CH switch)
2) if HW is on, both radiators and cylinder will be heated, but only until the cylinder thermostat is triggered
3) when 2 applies, the CH setting or living room thermostat have no influence on anything
I'm quite puzzled, because I cannot imagine of an explanation for this set of symptoms, given the fact that my system has two separate valves and a single pump (see pic).
Any suggestion on what could the problem be?
I also attach below a pic of the controller/programmer (SANGAMO 410, Form No.: 1).
Further details of the components:
- grundfos 59506180 (pump, left on the pic above)
- Honeywell v4043H1056 ( two-way control valve/diverter, bottom of the pic above)
- bgmvsp-2 (two-way control valve/diverter/actuator, top of the pic above)
I found some relevant discussions here and elsewhere, but they seem to deal with a three-way valve, which makes for a plausible explanation for the symptoms; however, my case looks a mystery to me.
Thanks in advance!
mbc
A recent problem turned up with my central heating.
It is a classical gas open vented system: gas boiler, loft cistern, indirect hot water cylinder, cylinder thermostat, living room thermostat, controller with separate knobs for hw and ch.
Symptoms:
1) if HW is off, nothing happens (irrespective of the thermostat setting and/or the CH switch)
2) if HW is on, both radiators and cylinder will be heated, but only until the cylinder thermostat is triggered
3) when 2 applies, the CH setting or living room thermostat have no influence on anything
I'm quite puzzled, because I cannot imagine of an explanation for this set of symptoms, given the fact that my system has two separate valves and a single pump (see pic).
Any suggestion on what could the problem be?
I also attach below a pic of the controller/programmer (SANGAMO 410, Form No.: 1).
Further details of the components:
- grundfos 59506180 (pump, left on the pic above)
- Honeywell v4043H1056 ( two-way control valve/diverter, bottom of the pic above)
- bgmvsp-2 (two-way control valve/diverter/actuator, top of the pic above)
I found some relevant discussions here and elsewhere, but they seem to deal with a three-way valve, which makes for a plausible explanation for the symptoms; however, my case looks a mystery to me.
Thanks in advance!