Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Central heating header tank expansion overflow in the Central Heating Forum area at Plumbers Forums

Status
Not open for further replies.
R

robo1889

Evening all
Had a call out today from a care home, hot water coming out of overflow.
It was from the f&e header central heating. I removed the lid and found the level was high and
Expansion was overflowing into the tank. The heating was on the rads were working fine and hot
water was also fine, as we're the motorised valves. I noticed the bottom stats on the cylinders (primary and secondary)
were loose and one had dropped off they seemed old so I put two new ones on thinking this was the
problem but its still discharging when heating is on. I also noticed the ball valve was full of water and heavy so drained
the tank and replaced the ball valve and got the level down to where it should be, the water was a bit sludgy
but I've seen worse. Could it just need a drain down and powerflush or is it pointing to the coil??
 
Last edited by a moderator:
Evening all
Had a call out today from a care home, hot water coming out of overflow.
It was from the f&e header central heating. I removed the lid and found the level was high and
Expansion was overflowing into the tank. The heating was on the rads were working fine and hot
water was also fine, as we're the motorised valves. I noticed the bottom stats on the cylinders (primary and secondary)
were loose and one had dropped off they seemed old so I put two new ones on thinking this was the
problem but its still discharging when heating is on. I also noticed the ball valve was full of water and heavy so drained
the tank and replaced the ball valve and got the level down to where it should be, the water was a bit sludgy
but I've seen worse. Could it just need a drain down and powerflush or is it pointing to the coil??
Before any other work, monitoring the the overflow situation would be my starting point. Based on the fact that the ball valve float was faulty, the problem may well be solved. Or the shut of water level and overflow height were to close to absorb the expansion generated by the heating up of the system.
 
Thanks for the reply I will pop back Monday and check it out not heard anything yet so no news = good news.
 
Status
Not open for further replies.

Similar plumbing topics

see same. below on this as some one has had...
Replies
1
Views
860
it is brand new ( 6 months old ) Worcester gas...
Replies
2
Views
682
losing pressure
L
I can't remember if I fitted one or not, but I...
Replies
4
Views
1K
Back
Top