Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Central Heating not coming on - Boss Therm BR1 Advice in the Central Heating Forum area at Plumbers Forums

Status
Not open for further replies.
D

DuNsTeR

Hi there,

I have a Boss Therm BR1 receiver with a BRTRF wireless thermostat. I believe the thermostat is communicating with the receiver as I can see green flashing and the orange light to suggest the boiler is on when thermostat temp reached but the boiler is not coming on. I have hot water perfectly fine.

The boiler is a Ideal Logic + 24kw Combi - Also I should mention the message on the boiler suggests room stat is turned off - when I can clearly see it is on and the receiver is suggesting it is on also and I can get the receiver to suggest it's on and off by playing with the room stat... as I say hot water kicks in fine everytime

hope that's helps and thanks in advance for any ideas....
 
Is the boiler on 'winter mode'? Sorry if that's bleeding obvious.

also check battery's, some rf stuff really struggled when battery starts to drop off
 
Is the boiler on 'winter mode'? Sorry if that's bleeding obvious.

also check battery's, some rf stuff really struggled when battery starts to drop off

Hi all I played some more last night and I think I have solved the problem as I managed to get the Central heating working by bypassing the BR1 unit proving that when the BR1 unit suggests it is sending a call for heat it isn't - I when I listen very carefully I can hear the microswitch/relay doesn't appear to be working - so I need a new unit and my boiler is fine... job done - thanks for stopping by
 
Relay broken . Same as Siemens unit. Common fault . Is it about 2 years old?

Buy new one exactly same from Pts ...... Wait about a week then take it back demand a refund. Swap base unit only as u can pair them. Put new cover back on old receiver in box. I can assure u I have never done this.
 
Last edited by a moderator:
Hello, just read this thread, ive got exactly same problem, same about 2 years old. Going to do the pts trick. Just to confirm, am i buying another BR1 part or the BPS242RF?
 
Status
Not open for further replies.

Similar plumbing topics

No you couldn’t need to be gas safe
Replies
9
Views
747
I have a home with an oil boiler in a garage...
Replies
0
Views
637
Sometimes the connection point of the cylinder...
Replies
3
Views
559
Its a Combi. Its a Worcester Bosch Greenstar...
Replies
8
Views
1K
Back
Top