Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Central heating not working 3 port valve? in the Central Heating Forum area at Plumbers Forums

Messages
94
Hi all,


Not posted for some time but come up against a small problem.
Been off the tools for many years now but I think I know the issue but looking for some reassurance
Boiler isn't firing when programmer and room stat is calling for heating, but does for HW.
It's a Y plan system, new house and only just noticed so not fully inspected.

From memory if the motor isn't working it won't turn to CH and send a signal out on orange to fire the boiler, am I right?
I don't know the type of valve, will check tomorrow but I guess it hopefully just a case of fitting a new motor?
 
Unless the microswitch Isn’t making, motor could be fine and microswitch faulty. Should get 240/230vac on the orange if making on switch. Could even be room stat, though unlikely.
 

Similar plumbing topics

In the end decided to follow Chuck’s advice...
Replies
11
Views
663
Sometimes the connection point of the cylinder...
Replies
3
Views
548
Replies
0
Views
446
https://www.NoLinkingToThis/p/drayton-27101sx-3-po...
Replies
1
Views
2K
I don’t think the connection on the detach pro...
Replies
24
Views
4K
Back
Top