Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Central Heating Pipework in the Central Heating Forum area at Plumbers Forums

Status
Not open for further replies.
L

Leoki

Hi All

If you have the time could you have a think about the following for me please, any advice would be gratefully received.

I am doing some work for a customer early in the new year, Im replacing 3 x existing wall hung steel panel radiators with newer compact radiators.

The loft in the property has been converted and I have been asked to put two compact radiators upstairs as well. It’s a large old Victorian style building so it’s a really nice loft space with windows at each end. One new radiator to go under each window. Distance between the front and back walls/windows is about 11 metres.

On the first floor there is the main family bathroom and 3 x bedrooms. The bathroom and one bedroom are at the back end of the house, each with an existing radiator in it, a bedroom in the middle of the first floor, the third bedroom being at the front of the house again with an existing radiator fitted.

I want to keep the length of pipe runs to a minimum, Im therefore thinking of coming off the flow and return (two pipe system) from existing radiators on the first floor in the front and back bedrooms, exposed pipework neatly running up the wall through the ceiling coming up into the loft directly above, under the window where the new radiators will be situated.

The house is served by a relatively new Worcester Bosch Greenstar Junior 24i combi boiler.

Any thoughts on this, any other observations. Cleaning of soldered pipework and inhibiting of the central heating system are already a given.


Thankyou
 
Last edited by a moderator:
I suppose that should work re pipe routing
Just be mindful of the system capacity re expansion as you havent said Whats already there.
If its already near the max re water volume you may need to add an extra expansion vessel.
Max is 100l
And also check pump head
 
Last edited by a moderator:
Newcastle Phill, thankyou. The system presently has 12 x radiators of various sizes connected, three proposed new ones would take that to 15 in total. The boiler has an maximum output of 24kw on the heating side. I will try and get some information from Worcester Bosch as to pump head values.
 
Status
Not open for further replies.

Similar plumbing topics

Fit one radiator, correctly sized to heat the...
Replies
7
Views
487
Replies
17
Views
2K
Since it became normal for trv's to be bi...
Replies
1
Views
582
You seem to have got it sorted, but for future...
Replies
7
Views
935
Hi Basher, Thank you for the reply. So the...
Replies
8
Views
794
Back
Top