Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Central heating sucking air through vent pipe in the Central Heating Forum area at Plumbers Forums

Jock Spanners

Plumbers Arms member
Plumber
Gas Engineer
Messages
208
Evening all,
I've just changed a Keston system boiler for a regular Worcestor with a pump. The customer had bought the boiler mistakenly thinking it was a like for like swap. I've added the pump and everything seemed fine but a week later he's complaining about air in the system and the F&E tank overflowing. I'd replaced the float valve and probably didn't bend the arm enough as there wasn't a lot of room for a 18 rad system. I've adjusted the arm further. I suspect the air is being sucked in through the vent. It's an S plan in a three storey house with the boiler and cylinder in a cupboard on the middle floor. The pump is on the flow pipe. The rads are all knackered and he didn't want a powerflush as he didn't think they would stand it. I agreed and tried to flush as much of the sludge out with detergent. I've turned the pump down. Has anyone any ideas what I can do? From distant memory I seem to think a 'wet vent' might be the answer but I can't remember how to do one. Any advice appreciated.

Jock.
 
You will have to close couple the feed / vent etc .
First pipe off the flow pipe , next vent , next pump . All within 150 mm .
Currently on the flow there's a 15mm stem pipe to an auto air vent above the boiler teed in before the pump. Are you suggesting teeing in the feed, then the vent before the pump and should I dispense with the stem pipe?
 
Currently on the flow there's a 15mm stem pipe to an auto air vent above the boiler teed in before the pump. Are you suggesting teeing in the feed, then the vent before the pump and should I dispense with the stem pipe?

I would yes , the close coupling system works . As said , feed first , immediately after vent , then pump , all on flow pipe , that wont suck any air in as its all under positive pressure . Ok a bit of work involved I will admit .
 
Like this?
Open-System-Header-Tank.gif
 

Similar plumbing topics

L
Replies
2
Views
2K
B
Context for issue: I'd like to start by...
Replies
0
Views
559
Butchy10
B
This was indeed the case, picked up a new zone...
Replies
13
Views
2K
OK, but from the boiler it should be Vent then...
Replies
16
Views
2K
Back
Top