Good afternoon,
Our system is losing pressure on a daily basis. Despite repeated top ups. I have listed the key points below.
I then top the system up to just over one bar and reset/switch on the boiler. The heating will work fine, however later the same day or overnight the pressure drops back down to zero.
2. When the motorised valve on the heating side is switched to MANUAL, the pressure is maintained, however the heating is on 24/7 but NO loss of pressure whatsoever
Now, our plumber has fitted, new valves next to the Megaflow where most of the pipework and pump are. Fitted a new expansion tank. Put a sealer into the system.
Still losing pressure on automatic but not manual.
Now, our plumber is telling us there must be a leak in the system under the floor downstairs. No sign of leakage upstairs. When I asked, why does it not lose pressure when the motorised valve is set to zero. He said, when the water is hot, it won't leak, it will leak when the system cools down. EH?
Could someone please tell me if this is true. I would have thought that hot water under pressure would leak out of a pipe quicker?
Before we start ripping the floor up to see if one of the pipes has a leak which will be no mean feat as we have 18mm solid Oak tongue and groove on top of 18mm OSB, I thought I would post on this forum to see if there is an alternative solution?
Thank you very much
John
Our system is losing pressure on a daily basis. Despite repeated top ups. I have listed the key points below.
- When motorised valve on the heating side is switched to automatic.
I then top the system up to just over one bar and reset/switch on the boiler. The heating will work fine, however later the same day or overnight the pressure drops back down to zero.
2. When the motorised valve on the heating side is switched to MANUAL, the pressure is maintained, however the heating is on 24/7 but NO loss of pressure whatsoever
Now, our plumber has fitted, new valves next to the Megaflow where most of the pipework and pump are. Fitted a new expansion tank. Put a sealer into the system.
Still losing pressure on automatic but not manual.
Now, our plumber is telling us there must be a leak in the system under the floor downstairs. No sign of leakage upstairs. When I asked, why does it not lose pressure when the motorised valve is set to zero. He said, when the water is hot, it won't leak, it will leak when the system cools down. EH?
Could someone please tell me if this is true. I would have thought that hot water under pressure would leak out of a pipe quicker?
Before we start ripping the floor up to see if one of the pipes has a leak which will be no mean feat as we have 18mm solid Oak tongue and groove on top of 18mm OSB, I thought I would post on this forum to see if there is an alternative solution?
Thank you very much
John