Hi guys, first post.

My central heating system is vented and very simple (pretty old setup, probably 20 years old) - no 3 way valves (multi-fuel boiler heats DHW through a gravity pipe leading up to coil in tank), and the CH is pumped from the boiler too (4 connectors on the multi-fuel boiler). I manually turn the pump on when there's enough heat.

There is only one feed, and one return pipe for the radiators.

Recently, I fitted a bathroom with underfloor heating (wet). The floor is less than 2 square meters. I concluded that since the piping for underfloor heating was short, I could test it out on the central heating circuit (after all, I thought the pump could handle it since the demand would be small and would be equivalent to adding another few radiators). There is only 5 radiators in the house.

I drained the system, and connected the underfloor pipes to the central heating return pipe (in series). Refilled the system (released air in radiators), put the fire on, switched pump on but none of the piping heated up (including the feed pipe). Pump SOUNDS like it's working. Gravity hot water supply is working perfectly fine as before.

I returned everything back to the way it was (took the underfloor piping out of the circuit). Refilled, put the fire on, switched pump on but still NONE of the pipes heated up (water not flowing). Pipes before and after pump aren't hot, same for feed pipe (until convection happens).

Each time I refilled, I bleed the radiators to release air. I have refilled 3-4 times now. Each time, there's plenty water in there and water is pretty clear (used to be sludgy).

Through some research I've found it's:

1) Probably the pump?
2) Airlocked? (have bleed the pump - not much air comes out)
3) Blocked?

Thanks in advance! :)
 
Update: Tapped on the pump (grundfos 15-50) and surrounding pipes, then the pump and pipe/flow leading away from pump got warm. Soon after, pump and pipe grew cold again.

Put screwdriver into pump, couldn't stop it, still span.

While refilling circuit, and/or connecting underfloor heating, some debris could have got into pipework/got dislodged and clogged somewhere - maybe somewhere at the pump?

Also, the feed pipe gets very hot leading up to about half way around the circuit where it gets less and less hot (convection?). And when I drain the system, as the water flows out it's cold up to a certain point, then it gets warmer and warmer from both ends (feed/return)?

This makes me doubt that there is a blockage...maybe impellers on pump are warn?
 
Last edited by a moderator:

Similar plumbing topics

  • Question
I have two rads upstairs connected exactly the...
Replies
22
Views
2K
There could still be 22mm pipework left...
Replies
5
Views
704
  • Question
Red circles show my new AAVs and the manual...
Replies
17
Views
2K
  • Question
You’re a genius, thank you! Held my thumb over...
Replies
2
Views
1K
Back
Top