Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Changing Expansion Vessel on Worcester Bosch 23i Greenstar in the Central Heating Forum area at Plumbers Forums

Status
Not open for further replies.
S

sadssandiford

Hi all usual symptoms;

Pressure ok when central heating off, shoots up to 3 bar when central heating on with usual water out of external pressure releif pipe!

Been told its Expansion Vessel that has failed!

Trouble is on Worcester Bosch 23i Greenstar Juniour, expansion vessel is part of boiler mounting frame!

As my flue goes out of boiler and straight through wall above boiler there isnt enough space to remove expansion vessel!

Boiler installation paperwork says if not enough room the boiler has to be taken off wall to change Expansion Vessel!

My question is cant you just disconnect horizontal part of flue from the elbow, slide flue out of way through wall, change Expansion Vessel and reconnect flue? Seems alot easier than taking boiler off the wall!

Any help much appreciated

Brent
 
Tried recharging the E.V? Had a few juniors that just needed pumping up, although also a few that needed replacing. You could always cut in an external.
 
Probably when someone rubbed off the other half of the 8 with a brilo pad or similar :D
 
Hi All, thanks for info, your obviously correct its a 24i Greenstar Jnr!

Just an update;

Checked pressure in Pressure vessel when system pressure at zero, Pressure Vessel shows zero, but no water at valve!
Pumped up Pressure Vessel to 1 Bar and system pressure also showed 1Bar!
Released system pressure by bleeding radiator to zero, checked PV pressure, now at zero!
To me this shows PV not holding pressure and failed!
But pumped up PV to 1 Bar, ran boiler and again system pressure upto 3 bar with PRV dripping water as one would expect with knackered PV!!!
Noticed radiators very hot so turned CH temp down from Max to 4 and pressure dropped to 2 Bar, with heating cycling!
Let CH cool down pressurised CH to 1 Bar using filling loop and ran system again!
This time pressure rose from 1 Bar to 2 Bar and when switched off and cooled, dropped to 1 Bar and stayed there!
Problem seemed to be solved, but all I did was turn CH temp from MAX to 4 so boiler not getting to 3 Bar!
Radiators still v warm so a bit confused!!!!!!!

Any ideas?????
 
Reading your last post you are out of your depth here.
Get someone in to sort this. As long as the vessel not burst they will be done in 30 mins.
 
Looking at your last post id say there are some fundamental properties of pressure that you dont understand and it looks that by chance you have solved the problem, id imagine if you now turn up your boiler you will find it is still ok.
 