I moved into my present 1990-built home just over a yearago. A British Gas (Potterton) non-condensingboiler was installed a year or so before I bought the property. All the rads have TRVs and there wasoriginally just a time-switch for boiler control. Despite recently installing a programmablethermostat in place of the time switch, I am finding it impossible to maintaina comfortable temperature in many parts of the property without leaving theheating on permanently. In frostyweather, even if I set the low temperature limit at 18degC it takes hours toget back above 20degC when the thermostat changes the set point.
Using an IR thermostat, I have found that the boiler flowtemperature is set at around 60degC. Iam guessing that this is because the return temperature is around 54degC. There is only around 5degC drop across therads even with the pump set to its slow speed. Am I right in thinking that the radiators would be more effective with a higher flow temperature?
I’m looking for advice . Is my short-term solution to increase the flow temperature and take ahit on boiler efficiency and my longer-term solution to fit bigger rads, or arethere other solutions?
Using an IR thermostat, I have found that the boiler flowtemperature is set at around 60degC. Iam guessing that this is because the return temperature is around 54degC. There is only around 5degC drop across therads even with the pump set to its slow speed. Am I right in thinking that the radiators would be more effective with a higher flow temperature?