Cold mains water hammer when taps are turn ON? | Bathroom Advice | Plumbers Forums
  • Welcome to PlumbersTalk.net

    Welcome to Plumbers' Talk | The new domain for UKPF / Plumbers Forums. Login with your existing details they should all work fine. Please checkout the PT Updates Forum

Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

American Visitor?

Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Cold mains water hammer when taps are turn ON? in the Bathroom Advice area at Plumbers Forums

Messages
14
The cold mains is in 22mm copper on a pipe run to to a bath and basin taps next to each other. The mains water is 4 bar static, no PRV or check valves. The bang happens seconds after the cold tap is turned on at either the cold bath or basin tap. There is a 0.5 litre potable water expansion vessel about 4 metres away prior to a combi boiler. There is a mechanical water hammer arrester 6 metres away close to the mains water stopcock. Don't want a PRV due to installation difficulties and the filter servicing required (very hard water). Given this, any ideas on the best way to resolve this please?
 
The shock arrestor should be fitted with a pressure reducing valve just after the internal srltop tap, or just after the first branch to allow full pressure at the first outlet (usually kitchen sink)
 
Thanks for the replies. Do pressure reducing valves require maintenance in a very hard water area?
Which make and model of adjustable pressure reducing valve is the most reliable, ideally fit and forget?
I don't mind pay out the extra for the reliability.
 
Thanks for the suggestion. I read the instructions for the Caleffi PRV here:
caleffi.com/sites/default/files/file/581035.09.pdf

Unfortunately, the instructions state the PRV cartridge needs cleaning at least every 12 months and a water hammer arrestor should be installed close by to prevent risk of damaging the PRV! Might be working perfectly for the first few years but several years later without being maintained, who knows. Does anyone know of a PRV that does not need to be maintained please? I believe there are some about but can't remember the manufacture name.
 

Similar plumbing topics

  • Question
take iso valves off and fit 1/2 inch x 22mm...