markbutcher355
I have a dead radiator. Its the one at the end of the run and the system is plumbed with 15mm pipe. The system pump was replaced two years ago. All the other radiators are fine. The feed pipe is hot to touch but the exit pipe is cold back to the preceding radiator.
The first thing I did was replace the thermo valve. The old one was fine. I opened the valve while I changed it - good flow. Then I took the radiator off and flushed it. Plenty of crud but good flow afterwards. I attached a hose to the exit side pipework and when I opened the valve some crud but again, good flow. I put it all back together bled the rad and expected heat. None. Just the same inlet pipe hot, exit pipe cold, radiator cold.
I removed the bleed and a good strong flow of water filled my bucket. The water got warm after a pint or four. Still no heat. No air lock, no blockage, valves OK. Rest of the system fine. I tried closing all the other rads and turning the pump to full speed, no change.
Anybody any ideas?
The first thing I did was replace the thermo valve. The old one was fine. I opened the valve while I changed it - good flow. Then I took the radiator off and flushed it. Plenty of crud but good flow afterwards. I attached a hose to the exit side pipework and when I opened the valve some crud but again, good flow. I put it all back together bled the rad and expected heat. None. Just the same inlet pipe hot, exit pipe cold, radiator cold.