Evening all.
I have open vented C/H system with a heat only boiler and 10 rads over 3 floors.
I have just replaced a rad on the middle floor. Drained system down for new gateway valve for cold feed for header tank. Refilled system no leaks, 👍, but the top top 2 rads won’t get hot.
ALL rads contain water, I have bled all rads. No hot water getting to flow pipe of either rad on top floor.
All other rads are working.
When I bleed the top cold rads, all I get is cold water.
Any ideas or help in helping me would be much appreciated
The top 2 rads are run in 15mm. All other rads get hot.
Cold Water actually squirts out of bleed valves in top 2 rads that don’t get hot. These 2 rads are about 10 years old. The others that all work fine are 24 years old.
Any advice would be much appreciated
Simon
 
Hi Simon, when you replaced the radiator, did you count the number of turns on the lock shield valve? You may have just upset the balance of the system.
 
Hi Simon, when you replaced the radiator, did you count the number of turns on the lock shield valve? You may have just upset the balance of the system.
I believe that rad that was changed, was a by pass rad and had 2 lock shields on it, so I did not count the number of turns. Maybe the system needs balancing. I am a DIY, so not sure how to balance the system
 
Ok. Firstly did you put a trv on rad or just change? Secondly try closing valves down all the way both sides and open 1/4 turn. Thirdly have a look here if you’re stuck:

 
Ok. Firstly did you put a trv on rad or just change? Secondly try closing valves down all the way both sides and open 1/4 turn. Thirdly have a look here if you’re stuck:

I bought a new rad, plus a TRV and lock-shield. When you say open 1/4 turn, is that just the lock shield valve.
 

Similar plumbing topics

You seem to have got it sorted, but for future...
Replies
7
Views
1K
The pin was stuck on the TRV,
Replies
3
Views
830
Thanks Chuck for the elaborate explanation...
Replies
10
Views
985
Me too. One pipe at a time, wet vac to hand...
Replies
4
Views
627
It is set to that, max output, CC3 at 6.5M...
Replies
19
Views
2K
Back
Top