I have a fault with a Baxi HE 133 combination boiler. I had a gas boiler engineer round to inspect it. He suggests that the boiler requires a new PCB electronic board. But I would like a second opinion, or as many informed opinions as I can get before forking out £200+ to have this done. I'll try and give as many details on the symptoms I can.
There are two symptoms:
1. After 10-20 minutes of operation the boiler shuts down and the indicator lights tell me that the boiler is "overheating". This is the light panel combination as according to the boiler manual. The engineer went through the checks in the manual for this fault and they were ok.
2. The water pressure is regularly dropping both when the boiler is fired up and when the boiler is idle e.g. during the night.
However, these issues are intermittent. If I close off most of the thermostats on the radiators and just leave 3 rads on then the boiler will operate perfectly well for up to 6 hours providing hot rads and does not appear to lose water pressure. I then open up more radiators and the verheating/drop in water pressure problems re-occur eventually.
I get the impression one of two things are happening:
1. Either the PCB and sensors are correct and the boiler really is over heating in which case insufficient water is entering the heat exchanger. Which could be a sticky or clogged valve?
2. Or the PCB and sensors are faulty and the boiler is not overheating and the electronics are giving a false reading. But if this is the case why is the water pressure dropping?
This is a link to the boiler manual
http://www.gasapplianceguide.co.uk/Baxi_HE_Plus_Range.pdf
Any advice welcome and a very merry Xmas to all
I have a fault with a Baxi HE 133 combination boiler. I had a gas boiler engineer round to inspect it. He suggests that the boiler requires a new PCB electronic board. But I would like a second opinion, or as many informed opinions as I can get before forking out £200+ to have this done. I'll try and give as many details on the symptoms I can.
There are two symptoms:
1. After 10-20 minutes of operation the boiler shuts down and the indicator lights tell me that the boiler is "overheating". This is the light panel combination as according to the boiler manual. The engineer went through the checks in the manual for this fault and they were ok.
2. The water pressure is regularly dropping both when the boiler is fired up and when the boiler is idle e.g. during the night.
However, these issues are intermittent. If I close off most of the thermostats on the radiators and just leave 3 rads on then the boiler will operate perfectly well for up to 6 hours providing hot rads and does not appear to lose water pressure. I then open up more radiators and the verheating/drop in water pressure problems re-occur eventually.
I get the impression one of two things are happening:
1. Either the PCB and sensors are correct and the boiler really is over heating in which case insufficient water is entering the heat exchanger. Which could be a sticky or clogged valve?
2. Or the PCB and sensors are faulty and the boiler is not overheating and the electronics are giving a false reading. But if this is the case why is the water pressure dropping?
This is a link to the boiler manual
http://www.gasapplianceguide.co.uk/Baxi_HE_Plus_Range.pdf
Any advice welcome and a very merry Xmas to all
Last edited by a moderator: