Im new to posting in this forum, but am having to resort to this as I need further opinions relating to this issue. I am pretty clued up (now!) so hopefully this all makes sense.
Starting approx 6 months back we started to notice that the pressure was dropping on our Worcester Bosch 28CDI boiler (combi). We topped the system up using the filling loop and bled the air out of the rads. Over a few months the pressure was gradually dropping faster and faster to the point that we are now losing virtually 1 bar overnight. This has now been the case for the few month and there is no sign of a leak.
We have had British Gas out using our homecare agreement and have tested all known possibilities.
Our pipework downstairs is buried under a concreate floor, so we have always suspected that the leak was somewhere there. But with nearly 6 months of leak, we thought there would at least be a sign or even smell coming through the laminate floor.
TWIST
I was getting fed up of topping up the CH a week ago and could not be bothered to bleed the rads after topping up. And for some reason the pressure did not drop so fast. Once the pressure dropped back down to zero (took 24+hrs), I topped up again to 1bar without bleeding the rads. The pressure seems to have stablised and has not dropped now in 3 days. Now this has really confused me as everything seems normal again, with the exception of having air in the system. I have checked all the rads and are hot top to bottom, so I'm not sure where the air is. Please someone make sense of this for me.
A few days back we had British Gas out again to quote us for a repipe/repair as our homecare only covers the boiler. Obviously this is a very costly proceedure and I just need some ideas of what we should do. If there is a leak, then we still have no idea where it is and this would require thermal imaging to locate (costly). Should we leave the system with air in and just assume that all is ok?
Your thoughts and suggestion would be a much need help
thanks in advance
Im new to posting in this forum, but am having to resort to this as I need further opinions relating to this issue. I am pretty clued up (now!) so hopefully this all makes sense.
Starting approx 6 months back we started to notice that the pressure was dropping on our Worcester Bosch 28CDI boiler (combi). We topped the system up using the filling loop and bled the air out of the rads. Over a few months the pressure was gradually dropping faster and faster to the point that we are now losing virtually 1 bar overnight. This has now been the case for the few month and there is no sign of a leak.
We have had British Gas out using our homecare agreement and have tested all known possibilities.
- There is no water for the pressure release pipe outside
- No damp pipework around the rads or boiler.
- Expansion vessle has been checked and was fine
Our pipework downstairs is buried under a concreate floor, so we have always suspected that the leak was somewhere there. But with nearly 6 months of leak, we thought there would at least be a sign or even smell coming through the laminate floor.
TWIST
I was getting fed up of topping up the CH a week ago and could not be bothered to bleed the rads after topping up. And for some reason the pressure did not drop so fast. Once the pressure dropped back down to zero (took 24+hrs), I topped up again to 1bar without bleeding the rads. The pressure seems to have stablised and has not dropped now in 3 days. Now this has really confused me as everything seems normal again, with the exception of having air in the system. I have checked all the rads and are hot top to bottom, so I'm not sure where the air is. Please someone make sense of this for me.
A few days back we had British Gas out again to quote us for a repipe/repair as our homecare only covers the boiler. Obviously this is a very costly proceedure and I just need some ideas of what we should do. If there is a leak, then we still have no idea where it is and this would require thermal imaging to locate (costly). Should we leave the system with air in and just assume that all is ok?
Your thoughts and suggestion would be a much need help