Hi,

We had a Valiant ecoTECplus 938 installed a couple of years ago. The past few months we've noticed it come on with the cold taps rather than just the hot. A plumber came to service it and said this is normal but we don't think it is + it's a waste of valuable gas. I've read up and think it might be a back pressure issue as the pipes do seem to slam when water is turned off. Any ideas or things to try would be greatly appreciated 🙂
 
Turn off the cold water boiler feed at the valve under the boiler. Then run a hot tap and see if you still get water.

If it’s a new problem/not historic, it’s quite possible that a thermostatic cartridge has failed and is allowing a cross over.

Isolating the hot supply and still getting water out of the hot taps proves this. Then you’ve got to find it. Usually a shower valve.
 