M
Masood
Morning all,
Went see a combi yesterday, a Main Eco. Problem is as follows - no issues with heating, hot water is great (flow and temp) at the nearest tap, cooler at the next furthest one, cooler still at the furthest one. It will run fine for a while, then the water gradually runs cold.
When she described the issue over the phone she just mentioned that the water was lukewarm, so I thought maybe the diverter valve was letting by, but having run the water, the CH flow pipe remains cold. So, I'm thinking blocked plate-to-plate? The reason I'm a bit hesitant is that the boiler is not kettling at all. It's a year old - too new to be choked up as yet I'd have thought, and there's a scale reducer fitted so limescale is probably not the issue...
Would you agree with my thoughts, or am I overlooking something?
Ta!
Went see a combi yesterday, a Main Eco. Problem is as follows - no issues with heating, hot water is great (flow and temp) at the nearest tap, cooler at the next furthest one, cooler still at the furthest one. It will run fine for a while, then the water gradually runs cold.
When she described the issue over the phone she just mentioned that the water was lukewarm, so I thought maybe the diverter valve was letting by, but having run the water, the CH flow pipe remains cold. So, I'm thinking blocked plate-to-plate? The reason I'm a bit hesitant is that the boiler is not kettling at all. It's a year old - too new to be choked up as yet I'd have thought, and there's a scale reducer fitted so limescale is probably not the issue...
Would you agree with my thoughts, or am I overlooking something?