Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Condense pipe is leaking under the boiler in the Boilers area at Plumbers Forums

Messages
9
Hi all

I have a newly fitted heat only boiler that is leaking at the point where the condense pipe enters the rubber fitting under the boiler. The siphon is not blocked and runs freely.

Any ideas?
 
It was only installed yesterday. My initial thought is a partial blockage in the condense pipe. Is that possible? Maybe water is backing up as the leek only happens when the heating kicks in on the initial fire up then stops. I had the thing running for over an hour yesterday with no problems whilst commissioning.
 
Solved!
As I suspected. Cut the condense pipe under the sink, outcomes the backed up water and what looks like grit, not my doing as always plug to stop that happening.
Drain clearing spring down the condense towards the kitchen sink waste and hey presto!
 
Solved!
As I suspected. Cut the condense pipe under the sink, outcomes the backed up water and what looks like grit, not my doing as always plug to stop that happening.
Drain clearing spring down the condense towards the kitchen sink waste and hey presto!

alu oxide? was the last boiler and alu heat exchanger ?
 

Similar plumbing topics

Hi all, Pipe moved...Temporarily fed back...
Replies
5
Views
686
In a one-pipe heating system with a condensing...
Replies
7
Views
467
G
Didn’t grease the oring before refitting...
Replies
2
Views
576
System boilers have a pressurised heating...
Replies
1
Views
266
Back
Top