Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Conditions of boiler install in loft? in the Boilers area at Plumbers Forums

Messages
29
I posted a thread last week about having had a boiler put in my loft.


Some people replied saying I needed to meet conditions to have the boiler in the loft, does anyone have a definitive list of conditions that I can present to my plumber and ask why I was never told about it?
 
TBH this says the same thing we have but you can show him this

 
Thought I would call Worcheter and ask, so they require:

  • Boarded up to and around boiler so someone can work on it.
  • Lights.
  • Fixed ladder.

And that's it - I guess this post can be closed, but thought i would update it for anyone who comes along in the future.


Thanks all for help.
 
The access, lighting and control requirements for installing a boiler in the loft of a property are clearly defined by the GS(IU)Regulations. They are not optional - just refer your installer to the regulations he is bound by.

He / she should be telling you the requirements not the other way round.
 
The access, lighting and control requirements for installing a boiler in the loft of a property are clearly defined by the GS(IU)Regulations. They are not optional - just refer your installer to the regulations he is bound by.

He / she should be telling you the requirements not the other way round.

Thanks, do you have a link online to these regulations?
 
Panther,

There are two key areas for this:

Regulation 28 (Access) of the Gas Safety (Instruction snd Use) Regulations state:

No person shall instal a gas appliance except in such a manner that it is readily accessible for operation, inspection and maintenance.

The second is BS 6798 which outlines the requirements for installing a boiler in a loft space:
Loft must be adequately illuminated with fixed lighting.

A permanent means of access must be provided to the loft ( a retractable permanently fixed loft ladder meets this requirement)

There must be a sufficient area of permanent flooring to provide safe access and working area; to, surrounding and beneath the boiler.

The floor or structure must be capable of holding the weight of the boiler in operation.

There should be a handrail around the loft hatch.

A guard / rail around the boiler to prevent material being stacked up against the boiler may be needed.

I am also fairly sure that there is a requirement that there should be provision to isolate the gas supply to the boiler without entering the loft space and to be able to control the boiler without entering the said loft space. At the moment, I cannot locate them - Duncan M may be able to help / give clarity on this point.

Not sure if the documents are available as free downloads, you can certainly access them on line as paid downloads.

Hope this answers your question.

A final point, these requirements for safe access are not “hidden” away in the legislation that your installer must work to. However, the access requirements must be in place before the boiler is installed in the loft area.
 

Similar plumbing topics

200% won’t be the reason the cylinder isn’t...
Replies
10
Views
1K
W
pcb issue so gas safe engy required sorry to say
Replies
1
Views
700
Thank you so much, that's very helpful!
Replies
4
Views
1K
GREENSTAR CDi CLASSIC Worcester Bosch...
Replies
3
Views
681
Back
Top