Hi all,
I've got 2x AHUs where I work with pre-heat coils after the filter on the supply ducting. These are heated using the boiler CT circuit. On both of these AHUs the method of control of heat to the coil is a 3 port mixing/diverting valve with the central port blanked off. There doesn't appear to be any bypass pipework on these coils, apparently it used to be a 2 port control valve controlling the pre-heat coils on these AHUs.
I've already worked out both valves are faulty, they are passing significant quantities of water when the BMS is calling for them to close fully. Winding them forward and back hasn't helped.
The question is, is a blanked off 3 port valve sufficient to control these? Temperature just after the pre-heat coil is fluctuating by +/-10C on one AHU and +/-5C on the other AHU so something is pretty badly wrong! Especially as they shouldn't even be on at this time of year
Question is, am I right in thinking AHU heating coils should be controlled by a 3 port mixing/diverting valve rather than a 3 port valve with the middle valve blanked off? It would be relatively simple to fit bypass to the heating coil return if there's an advantage in doing so.
Also, can anyone explain why the valve appears stuck open but the temperature is fluctuating up and down so much to both AHUs?
I've got 2x AHUs where I work with pre-heat coils after the filter on the supply ducting. These are heated using the boiler CT circuit. On both of these AHUs the method of control of heat to the coil is a 3 port mixing/diverting valve with the central port blanked off. There doesn't appear to be any bypass pipework on these coils, apparently it used to be a 2 port control valve controlling the pre-heat coils on these AHUs.
I've already worked out both valves are faulty, they are passing significant quantities of water when the BMS is calling for them to close fully. Winding them forward and back hasn't helped.
The question is, is a blanked off 3 port valve sufficient to control these? Temperature just after the pre-heat coil is fluctuating by +/-10C on one AHU and +/-5C on the other AHU so something is pretty badly wrong! Especially as they shouldn't even be on at this time of year
Question is, am I right in thinking AHU heating coils should be controlled by a 3 port mixing/diverting valve rather than a 3 port valve with the middle valve blanked off? It would be relatively simple to fit bypass to the heating coil return if there's an advantage in doing so.
Also, can anyone explain why the valve appears stuck open but the temperature is fluctuating up and down so much to both AHUs?