Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Correct Expansion Vessel Pressure in the Central Heating Forum area at Plumbers Forums

Messages
3
Evening all,

So I've been losing pressure from my boiler on a daily basis and having to top it up. The pressure gauge is up at around 3.5 bar when the boiler is on so I assumed the expansion vessel has either failed or is low on pressure. I had a look on both the Cimms website (the EV is a Cimm RP250 10 litre) and it shows that it requires 1.5 bar of pressure. The sticker on the EV shows 0.8 bar (I think). Anyway, to stay on the safe side I decided to stick around the 1 bar mark. I checked the shraeder valve and air came out with no water which seemed promising. I topped it up to 1 bar and then tried again but there's no difference. It took very little to fill it to one bar (about 1 second) so I'm assuming the correct pressure is 1.5 bar. Any thoughts?

Thanks

Steve
20210106_114745.jpg
Screenshot_20210106-114511_Drive.jpg
 
What pressure are you running the system at?
Did you de-pressurize the wet side before charging the dry?
The wet side needs to remain at zero pressure whilst charging the dry side.
 
What pressure are you running the system at?
Did you de-pressurize the wet side before charging the dry?
The wet side needs to remain at zero pressure whilst charging the dry side.
The system usually runs at around 1-1.5 bar. Yeah I de-pressurised the heating circuit and then isolated the flow and return. The pressure gauge rose to 1 bar as I charged the EV. Not sure if that answers your question but thanks for the reply.
 
The system usually runs at around 1-1.5 bar. Yeah I de-pressurised the heating circuit and then isolated the flow and return. The pressure gauge rose to 1 bar as I charged the EV. Not sure if that answers your question but thanks for the reply.
You need to pressurise the dry side and use a gauge on that side.
No pressure should be allowed to build in the wet side as you charge it.
I would charge it to 1 bar.
If this is internal to the boiler you are supposed to be gas safe registered. Did you know that?
It looks on the photo as the vessel is on the rear?
 
You need to pressurise the dry side and use a gauge on that side.
No pressure should be allowed to build in the wet side as you charge it.
I would charge it to 1 bar.
If this is internal to the boiler you are supposed to be gas safe registered. Did you know that?
It looks on the photo as the vessel is on the rear?
Thanks mate. No I wasn't aware. I'll get someone round to take a look. Thanks for the advice.
 

Similar plumbing topics

it is brand new ( 6 months old ) Worcester gas...
Replies
2
Views
680
losing pressure
L
D
Hi all, My pressure is stable at 1.5 when...
Replies
0
Views
298
Damo666
D
Pin hole leak on suction side of pump.
Replies
1
Views
465
Hello, I live in a two floor semi with a...
Replies
0
Views
763
A
As above 1 bar is more than enough vallants...
Replies
2
Views
628
Back
Top