Monkfish
Hi, I had a new boiler installed about 5 months ago. The plumbers ran a new 22mm copper pipe from the gas supply alongside the existing 22mm copper pipe for the flow and return (30 years old).
Since the installation I have been losing around 1/10 bar pressure per week (sealed system) and have been topping up the pressure thinking that the system was just taking its time to stabilize. I was slightly worried it might be a small leak, but as I could find no signs I ignored the pressure drop.
This week I noticed the telltale sign of water dripping from a light socket. Investigating, I found a floor beam that was soaked just where the three pipes mentioned above passed through it (inconveniently right under a partitioning wall).
Further along the pipe I noticed a small bead of flux had been left bridging the return pipe and the new gas pipe. Cleaning off this flux I noticed a small pin hole in the return pipe (which later investigation revealed was about to breach the pipe). Thankfully, there was no such hole in the gas pipe (which seems strange as both are copper). Cutting out the pipe from under the wall revealed similar flux residue and many more holes (as shown in the image). This was the source of the leak.
Now I could have imagined that the return pipe which is over 30 years old had slowly corroded under the wall and the new pressurised system finally forced the water through, but the hole further up was clearly caused by a bead of flux left during the upgrade 5 months ago.
Is it normal for a small bead of flux to eat its way through a copper pipe in this period of time or could there be some additional electrolysis action between the gas pipe and the water pipe (both are earth at the boiler)?
Since the installation I have been losing around 1/10 bar pressure per week (sealed system) and have been topping up the pressure thinking that the system was just taking its time to stabilize. I was slightly worried it might be a small leak, but as I could find no signs I ignored the pressure drop.
This week I noticed the telltale sign of water dripping from a light socket. Investigating, I found a floor beam that was soaked just where the three pipes mentioned above passed through it (inconveniently right under a partitioning wall).
Further along the pipe I noticed a small bead of flux had been left bridging the return pipe and the new gas pipe. Cleaning off this flux I noticed a small pin hole in the return pipe (which later investigation revealed was about to breach the pipe). Thankfully, there was no such hole in the gas pipe (which seems strange as both are copper). Cutting out the pipe from under the wall revealed similar flux residue and many more holes (as shown in the image). This was the source of the leak.
Now I could have imagined that the return pipe which is over 30 years old had slowly corroded under the wall and the new pressurised system finally forced the water through, but the hole further up was clearly caused by a bead of flux left during the upgrade 5 months ago.
Is it normal for a small bead of flux to eat its way through a copper pipe in this period of time or could there be some additional electrolysis action between the gas pipe and the water pipe (both are earth at the boiler)?